Hello,
after updating to 3.51 i noticed a strange phenomenon regarding the input current limit settings on the Venus OS UI.
On my three quattros i’ve set the function “override by remote” for the input current limit. It is actived for both inputs.
If i switch form grid to generator i can adjust the input current limit and it works as intended. If i now disconnect the generator and switch back to grid supply, BOTH input current limit settings for grid and generator are greyed out and cannot be changed anymore. Venus OS states that they are fixed in the system configuration.
The only way to fix it for now is to restart the cerbo gx. After a restart it works again properly as long as i do not perform a change of input. If i change to generator and back the issue manifests again.
System configuration is three-phase ESS with three Quattro II 48/5000 and a Cerbo GX.
With older firmware - i.e. 3.3.x or 3.4.x everything works fine. With 3.51, as well as 3.52 there are the discribed issues.
Does anyone else have this problem?
Thanks very much in advance!