VE.Direct Inverter 12/1600 220V. Overload alarm trips at 380 W

I have the aforementioned inverter installed with 25 mm² cables, 40 cm from a 320 Ah LiFePO4 battery. It has Bluetooth and a Victron remote control.

In On mode, it works properly with a 700 W sandwich maker, a TV, phone chargers, etc.

But I was surprised when I connected a 380 W hairdryer: the overload alarm goes off and it stops inverting. It doesn’t switch off, and I stay connected via Bluetooth.
The voltage before switching on the load is 13.33 V. When I connect the hairdryer, the voltage drops to 12.96 V and the load is 381 W. After a second of running, the alarm goes off and it stops inverting.

I’ve confirmed that it does the same thing with a 47 W hair straightener. But it works properly with the 700 W sandwich maker.

I’d appreciate any help. Thanks

A known issue :grimacing: … Some hairdryers work perfectly, while others only work on a higher setting. In short … it’s a very difficult and “dirty” load for an inverter, as it doesn’t draw a clean sine wave. Hairdryers often reduce the speed and heat using a simple diode and capacitor … So, two problems at once … a clipped or half sine wave, and a capacitive load … So it’s worth trying a higher heat setting. Otherwise, there’s really only one thing to do … Keep trying :innocent:

Hello Carlos,

What settings did you use to program the inverter?

Please try it with a standard fan heater at 1,000 watts and then 2,000 watts, and watch the display.

Victron inverters are usually very forgiving and can handle significant overloads.

I wouldn’t connect 2000 watts to a 1600W inverter…

The MultiPlus 12/1200 handles a 1750-watt kettle with no problem

The manufacturer specifies 130% for 30 minutes, and even more for short periods

Good evening.

Thanks for replying. I’ll try another hair dryer.

The hair straighteners. Maybe they’re 47 W.

With the old inverter, which wasn’t a Victron, this didn’t happen.

Regards

If they are anything like my mother in law’s hair straighteners, those things have the most evil power regulation circuit in them (triac regulated), with an oscilloscope it’s easy to see why there would be an overload. Sharp spikes from triac firing, capacitor charging in the snubber circuit, or an asymmetric (half-wave) current will have something to do with it.
So the most likely explanation is the sine wave is being chopped up alot and there is back emf into the inverter.

If you run the sandwich machine (or other resistive load) and the hair dryer it very possibly won’t shut down. Or the hairdryer and straighteners not on a lower setting.