3x2 Multiplus 8kVA (S99) parallel setup, house is connected only to the Output.
VM-3P75CT
SmartSolar 450/200
214kWh LFP (7 packs)
Incoming for charging
8.5kW PV power AC
2.3kW PV power DC
21kW Grid power AC
On V3.80~4 Grid keeps nicely appr. 21kW power appr. 30A per phase.
On V3.80~7 Grid charging seems reduce on a phase, for example L2 if L1 & L3 loads are pulling a bit more, it seems related to ~7
In ~4 Grid charging power is untouched, does not matter how loads are shifting.
Example behavior V3.80~4
Grid appr.
L1 30A 7.0kW
L2 30A 7.0kW
L3 30A 7.0kW
Loads
L1 1.1kW
L2 0.6kW
L3 1.3kW
Example behavior V3.80~7
Grid appr.
L1 30A 7.0kW
L2 24A 5.5kW
L3 30A 7.0kW
Loads
L1 1.1kW
L2 0.6kW
L3 1.3kW