Hello,
I’ve posted a few ideas earlier and taken on-board feedback, specifically using a 5000VA unit purely for its motor-starting capacity. I’m closer now to purchasing parts so just need a sanity check. We’ve already covered the load application in my older posts - a 1.25 kW (230VAC 5.2A) water pump that runs intermittently during rainfall. Power must be maintained to that under all circumstances without human intervention. There’s a backup pump but I don’t see that both would ever run together.
I’m happy that the battery is large enough from an energy perspective. I’m hoping it’s also enough for the MP2 from a start-up power perspective, that being 250ms.
The 5kWh 48V LFP battery will have a 125A fuse and 100A CB acting as an isolator.
In the PDF drawing it’s the stuff in the box at the lower-left that’s relevant, along with some house rewiring to exploit the UPS past just supporting the pump.
As I’ve explained in the drawing notes I’d like to use a generator-type ATS around the Victron AC input and AC-1 output to bypass it automatically if for any reason it’s not outputting AC when the grid is down. It’s the same switch model I use for my existing generator system and works well in that application. In this case the neutral is passed around it to maintain the MEN.
The MP2 will feed the existing generator/ATS system which will simply pass it through to the pump. In the case where no power is provided the generator/ATS will automatically handle pump power requirements. That system is proven but the long term goal is to remove it and rely solely on the MP2 and battery once I become confident of its reliability.
- I need to be confident the Victron application is feasible before I call my electrician as they will bill me for any time they spend on it. I’m fairly confident they will be happy with this wiring arrangement but doubt they know anything about commissioning an MP2. I’ll have a USB cable on hand and a PC with the config program. As best as I know my grid provider (“lines company”) requires an application to be lodged for every install but I know they already ‘type-approve’ the MP2.
- Legally I can’t use grid power for my own initial testing. As such, is it feasible to set the mains input to the non-specific setting initially so that I can test functionality (charging the battery, switching to inverter output, etc) using my (alternator-type) generator as an off-grid system?
- Once that’s done, my electrician would wire it to the house, configure it for “NZ-grid” and sort out the paperwork.
- As I’ve mentioned in my other posts my grid power is very reliable. If the MP2 is needed the pump will run intermittently, just 1 minute per each 3 mm of rainfall. I’m confident the cabinet cooling will be adequate even if it were in continuous operation.
29-06-2026 Block Diagram.pdf (4.4 MB)