I just set the ESS to “Optimized with battery life” and the system starts charging the battery (21%) from the grid as expected. However, VRM and Victron Connect display “Discharging”. The battery is busy charging, everything works as expected. Right now at 40% and increasing, all fine.
Mind sharing the VRM id (the number in the url from the vrm dashboard), so I can have a look at it?
I expect there is a configuration error somewhere.
I found the id already. The battery is really charging, only the display is wrong. Above about 328 A (roughly 18 kW) your BMS’s current value overflows and turns negative, so it shows as “Discharging”. SOC and charging are fine.
Could you tell me the battery model, the BMS firmware version, and which BMS/CAN profile is selected on the GX?
Good morning, I tried to answer to your mail, but it says:
We’re sorry, but your email message to [“notifications@victron.discoursemail.com”] (titled Re: Victron Community: The display in VRM and Connect is wrong regading charging/discharging) didn’t work.
You don’t have permissions to reply to the topic. If you believe this is an error, contact a staff member.
However this is what I tried to send:
Hello,
the IDs:
VRM Portal ID
48e7da85e17f
VRM Site ID
258224
after setting ESS to “Optimized with battery life” it started charging at 515A. I reduced the charge to 400A because that is what the two RS450/200 can do.
The 515A were the highest current ever, and it was not intended. The last time I had enough PV to reach 395A charge, the display showed the correct values then. I recently updated the Cerbo GX and RS450 software. I haven’t got to updating the MP II 15000, the MK3-USB cable didn’t want to cooperate.
The batteries are from Liontron, under “Advanced” it says max charge/discharge current is 690A, which I never intend to reach. There are no more details about the BMS shown.
Remote access is activated.
Hi @Ulrich_Scheper , I had a look at your site. This morning it seems to be behaving differently to what you described. It is reporting positive power which rougly matches what the MPPTs are making. Did you change anything?
The charge/discharge indication is driven simply off the power reading we get from the battery. If that is more than 30W positive, it assumes the battery is charging. If it is more than 30W negative, it will show discharging.
The SOC and system control are working as they should. The display issue comes from the Liontron BMS: above about 327 A, the current value it sends to the Cerbo rolls over to negative. The Cerbo shows that value as received, so VRM shows “Discharging”. It’s best to report this to Liontron so they can fix it in the BMS firmware. Until then, a DVCC charge current limit just under 320 A keeps the display correct.