This is confirmed at MPPT Solar Charger Error Codes [Victron Energy] where it says additionally that this error will flash only when solar power is available and the MPPT is ready to provide charge current.
Based on MPPT solar charger documentation, this alarm should show up on the MPPT solar charger with the absorption led flashing.
I have a system based on a Multiplus II GX 3000/32/35 with MPPT Blue solar 150/45 and 3 Pylontech US2000C, configured on ESS, all firmwares uptodate.
I checked the set up in the MPPT and it shows BMS control.
All working well.
However, when disconnecting the VE-direct connection between the Multiplus and the MPPT, nothing happens immediately on the MPPT. After a short while (about 1 mn) the MPPT goes to float mode (the Float led lit fixed) (even during day time with solar power available). The #63 alarm never shows up.
Is this normal behaviour ?
If yes may be the relevant documentation should be updated.
If the MPPT goes in Float mode when BMS control is lost, what Float voltage is used ? The one configured in the MPPT ? What value should we have here ?
I had a similar case with an RS450/200. In this case, disconnecting the CAN bus caused the MPPT to immediately switch off the charge controllers, which was fine. However, error #67 was not displayed; a different error appeared. That was OK.
Disconnecting the BMS CAN connection to the GX, however, caused the RS450 to regulate its output to 100%, which is absolutely not OK. I couldn’t trigger #67. I checked all the parameters (BMS control enabled, controlling BMS explicitly selected, etc.).
After I updated all the firmware versions, #67 was displayed correctly and the charge controller regulated its output to 0.
These faults should definitely be tested to check that everything works correctly: both the GX-to-charge-controller connection and the BMS-to-GX connection.
Thanks for your comment. In my case all firmware are uptodate. Disconnecting the VE-direct connection, which serves as BMS connection, does not generate any alarm, but only passing to Float mode whatever the batterie SOC is. This means current is reduced to nearly 0 and the MPPT only maintains the battery SOC during daytime.
Let see what feedback we may get from Victron staff if any.
Thanks Matthias for the feedback and confirming the 1 minute delay is OK.
My MPPT has no Bluetooth indeed, but looking at the official Doc, any error status is shown by flashing the absorption led. In my case I get the float led fix.
So the MPPT is not in error just stopped.
If this is normal behaviour, this is fine for me as it is a safe mode, but it is not aligned with the Victron/live documentation. Additionally, I do not figure out what bulk voltage is applied as the MPPT is configured to be controlled by BMS and BMS is missing. I will check the DC voltage at the Multiplus connections during the test.
I do not know how to report for the doc to be adjusted. I thought this was the proper channel.
You should also check logs. Error 67 might be there, because it does show up when I reconnect the MPPT to the GX device. I.e. when I disconnect the MPPT, nothing happens, when I connect in back, I immediately get both the alarm email and the alarm clear email.