takes energy from grid. But set ESS optimized and battery soc 15% . Have any ideas?
Is all your firmware up to date?
Switch your phase regulation to individual phase.
Reboot the GX
set Individual phase, reboot , wait, no effect( Looks like a bug.
All firmware update, multiplus v 3.75
Is DC feed-in enabled? Does your grid code allow for it? Do the batteries allow for discharge, in DVCC?
You are using the MP itself as the grid meter, then why is the grid power chart so spotty? Is your grid that unreliable or your communication?
The problem was the voltage stabilizer. I’m in shock.