Hi there!
We recently finished setting up an on-grid system for our home which consists of:
3x Multiplus II 48 / 5000 / 70-50
4x US5000 Pylontech batteries
1x SolarEdge ~13kW PV inverter
2x Lynx Distributor 1000
1x Ekrano
1x VM-3P75CT ( not connected yet )
The overall wiring goes in the order of
PV Inverter & House loads > AC Out
Grid > AC In
Lynx > You know where it goes to… ![]()
Ekrano has all devices except the Lynx connected to itself.
All multiplusses have the same ESS assistant and same same settings across each other.
ESS is correctly as for what we know configured in the multiplusses ( PV Frequencies, Is connected to AC Out ? yes, DC voltages are checked)
Ekrano has the latest ( beta & large ) version of venus.
ESS is set mostly to default, Mode 1( Optimized + BatteryLife ), Minumum SoC 20%, self-consumption(which we cannot change ?), Grid setpoint 20W, AC-coupled-PV - feed in excess is enabled)
ESS work completely fine, loads, discharge and manages all of the system.
BUT.
Why does ESS waste a lot of energy to the grid, whilst it is intended for own use ?
From what i have heard, i could just turn on AC Ignore and therefore disconnect the grid.
BUT i have also heard from a Victron technician that switching the relays overtime would cause more “stress” on the relays and could therefore potentially fail way more earlier than it was likely intended for, as the current system, doesnt switch any of the relays at all ( unless the grid fails ofcourse )
Is it a problem to us? Not really, but it seems strange, as it is not a phase compensation ( by the looks of it )
who knows something about this mystery ?