Surplus Injection Issue with Multiplus 24/2000/50 and Grid Code Standard

Hello, I hope you are doing well.

During the installation of an ESS on my Multiplus 24/2000/50, I need to select a grid code standard. However, regardless of the grid code I choose, I receive the warning: “This device is not equipped with internal interface protection”. The only exception is when I select “Other: not compliant to any grid code standard”, but in this case, I cannot inject energy into the public grid. As a result, the photovoltaic inverter automatically reduces its output power.

Can someone help me resolve this issue so I can inject the surplus energy?

If memory serves me, the multiplus only has single input relays, so cannot be used/certified for ESS purposes as regulations require dual relays for safety.
The MP2 and Q2 all have dual input relays.
As shown on this block diagram.