I want to map out a schematic for a dual inverter system for split-phase 240V using Multiplus-ii 5000/48v in a grid-tied North America setup using the existing panel with a 200 amp service and all loads connected to the existing breakers. This would be a non-solar setup (for now…) I would want to connect the inverters to the existing panel with a dual-gang breaker and then put a current clamp on for each leg of the split-phase of the Grid main’s 200A 4/0 wires that come into the panel. The Multiplus-ii would be setup in grid-tied ESS mode and configured to charge the battery and discharge the battery back to the grid to offset time-of-use billing. The goal would be never sending energy back to the grid, but nulling out the grid use to near zero during the peaks. I believe in this case you can use the current clamp port built into the Multiplus-ii and put it on the mains. What current clamp would you use for the 200A capable mains?
In the case when the home load is exceeding the capacity of the inverter, the grid would just make up the difference past the capacity of the inverter. I believe all that is needed in for this to work is to connect the Grid to the input AC port and then the output AC ports would be not used.
Anyone have any reasons why this won’t work?
What happens in this setup during a power outage? I think I’d rather figure out how to connect the whole panel to the output of the inverter rather than to guess which circuits I’d want to stub out during a grid failure. I’d rather have a manual disconnect or main panel lockout breaker based transfer switch to deal with a power outage rather than re-route a subset of (critical loads) to the output of the multiplus-iis secondary AC outputs. During a power failure, I’d like to run all the lights, the dryer, the oven, the car charger, the heat pumps, the space heaters… all off the inverter, just not all at the same time, and I’ll manage it myself with the manual transfer switch.