Hiya,
Have an off grid house system and am just adding two new 25.6v 200ah batteries to the BMS. It’s a 48v system and I now have 6 batteries (3 sets of 2x25.6v 200ah wired together and each into 1 of the ports on my lynx 1000 to create the 48v). I can’t find a solid answer on what I should be detailing in my BMS settings for this.
Should it be:
Battery bank voltage : 48v
Battery bank capacity : 200ah
Number of batteries in parallel : 6
or
Battery bank voltage : 48v
Battery bank capacity : 600ah
Number of batteries in parallel : 3
Or neither of the above and something else entirely?
Any help would be really appreciated!
To make 48v from 25v batteries you series them. So 2 in series.
But since you have 6 it is 2 in series 3 in parallel.
Your capacity will remain the same.
Is each 25.4v battery 200Ah?
If so you have 30, 480kwh of battery (6x 25.4v x 200ah)
At 48v it is still 30 480kwh of battery but you have 3 (strings)x 200ah - 600ah of battery. (3x (25.4v x2) x 200ah)
1 Like
Hi,
Thanks very much for your help with this. Ah sorry yeah so 3 parallel sets of 2 in series.
Yeah uh huh, each of the 6 batteries are victron life po4 25.6v 200ah.
Does that then mean on the BMS settings the values should be changed to
Battery bank voltage : 48v
Battery bank capacity : 600ah (or 200ah)
Number of batteries in parallel : 3
Again, much appreciated
Brilliant, thank you very much!