I have 4 200ah lithium NG batteries wired in series parallel for 24v system. How do I correctly setup BMS for -Number of batteries-Number in series-Number in parallel?
I think it should be 4 batteries, 2 series, 2 parallel… Thats not how my tech identified them.
Check that the battery communication cables have all been connected together properly in one loop from the BMS, through all batteries and back to the BMS.
Secondly, I wonder if the system was started up with only 2 batteries, then the other 2 connected. It might be worth trying a reset to default in VictronConnect to initiate another auto detect.
Closing the loop. I reset the BMS to default with no change. Disconnected the communication cables and started over. I must have had a cable incorrectly routed. All works, now displaying. 4 batteries 2 series, 2 parallel, 400Ah.