Large Battery Bank

Hi All,

Looking for guidance as I increase my battery bank capacity at the off-grid camp.

At present, I have 3x 170Ah Victron Super Cycle AGM batteries in parallel (diagonal wiring), and I plan to add three additional, identical batteries.

Victron does not seem to indicate if there is a maximum number of AGM batteries in parallel, and my concern is imbalanced loads/charging. All wires (4/0) are of equal length in between the current three batteries. As I see it, there are three options for which I am looking for feedback:

  1. Connect three additional batteries to the existing parallel string, maintaining diagonal wiring.
  2. Create a new, 3x battery parallel string, and connect this via Lynx Power-In, staying parallel with the original bank.
  3. Divide batteries into three groups of two, connecting each two-battery parallel string into the Power-In bus bar, all ultimately in parallel to maintain 12v output (I’m thinking this would ensure most consistency in battery load/charging).

**Note that regardless of the option chosen, all cables will be the same gauge and length.

Appreciate the feedback!

About half way trough the battery bank chapter you see four examples.

If you are thinking about going from 12V 510Ah to 12V 1020Ah then i think its worth also worth thinking about switching to 48V if you are in the business for that kind of capacity

I agree with the recommendation for 48v…just trying to avoid that as to not have to replace the Multiplus 12/3000/120.

If the MP is the only thing that would need changing, then thats manageable

To your initial question, i like the fourth option, to me its the simplest to use and wire up

1 Like