First post, I am new to Victron and these systems. I have a 50A RV with a Victron MultiPlus II inverter/charger and Cerbo GX, professionally installed by others January 2025 along with 1600 W of solar and (2) Victron MPPT. The coach also has a factory Onan Marquis Platinum 6500 LP generator (single-phase, 2 x 30A onboard breakers) that’s worked flawlessly for 20 years.
On 50A shore power, everything works perfectly — both L1 and L2 show on the Cerbo and charging works as expected. But I’m seeing issues on any single-phase source:
• 30A shore: Cerbo display shows “Shore Disconnected” (at least for one leg), sometimes charging occurs but I also get VE.Bus System [276] Overload L1: Warning in VRM alarms.
• Generator: No charging at all, Victron doesn’t seem to register AC input.
• 15A/20A outlet: Using standard adapters from my 50A plug down to a household outlet, the Victron won’t charge at all.Installer suggests this is a "bonding problem" somewhere in my RV's wiring.
• Ford Pro Power 120V outlet: Plugging in immediately trips the truck’s outlet into error mode. I’ve heard this may be related to neutral–ground bonding. I will pursue this challenge separately but I include here as background.
When I was using 30A shore power and experiencing the Shore Disconnected message, my installer remotely determined the system was “working” (=charging) despite the erroneous disconnected indication. Later, a separate source suggested that the overload warning might indicate on single-phase sources, only L1 is powered and all loads are stacked there, and with L2 unused, that the Victron is wired/configured for 50A split-phase without an L1–L2 tie when on single-phase inputs (30A shore, generator, small outlets).
Questions for the group:
1 How should the Victron’s AC inputs be wired so that single-phase sources feed both legs?
2 What’s the correct Victron configuration for switching between split-phase (50A shore) and single-phase (30A shore, generator, small outlets)?
3 If all components are installed and configured correctly, are there any known "glitches" that would cause the system to report incomplete or erroneous information? Am I unreasonable to expect this system to operate and display flawlessly and automatically as I move between 50A, 30A, 20A shore power and inbuilt generator?
4 Is safely running the Victron from my Ford Pro Power 120V outlet without tripping it related at all or should I pursue that separately?
Equipment:
-
Inverter/Charger: Victron MultiPlus II 12/3000/120-50 (FW 2780552)
-
Charge Controllers: 2 × Victron SmartSolar MPPT 150/60 (FW 3.16)
-
Monitoring: Cerbo GX with Touch 50 (FW v3.60)
-
Batteries: 10 × 105 Ah Lion Safari UT 1300 (LiFePO4)
-
Solar: 1,600 W roof array (8 × 200 W Renogy panels)
-
Generator: Onan Marquis Platinum 6500LP, auto-start via Onan EC-30
-
Shore Power: 50 A
-
Other relevant gear: Battery Heating System, Hughes Autoformer, Surge Guard RV Power Monitor #34750
Thanks for any guidance — I’d like the system to work seamlessly from all AC sources without overload warnings or missing charging.