Hello everyone. I have a 3-phase system with 6x MultiPlus-II 5000VA (2 units in parallel per phase) running on firmware v560, with a Cerbo GX, Batrium BMS, and a 20kW Fronius on AC Out 1.

I am looking for a configuration that allows me to replace a hardware solution I am currently testing. I have frequent grid drops caused by grid overvoltage during very sunny days. These outages are usually short, and I want all my loads on AC Out 2 to be covered by the battery during these brief moments. If the outage lasts longer than 30 minutes, I manually or automatically disconnect them to switch to a generator via an ATS, but that’s a separate logic I handle in Node-RED.

Right now, to make this work, I am testing a single 6-pole relay with isolated contacts triggered by the Cerbo’s Relay 1. I went with this hardware setup specifically to avoid putting the AUX inputs in direct contact with each other. I felt it was a necessary precaution to keep the Cerbo isolated from the AUX ports and to ensure the AUX inputs of all 6 units stay electrically separated from one another to avoid any interference or potential issues. This relay closes the AUX 1 input on all 6 MultiPlus units at the exact same time to ensure they all toggle their AC Out 2 relays simultaneously and avoid any sync errors.

I would really like to get rid of this physical relay and all the extra wiring by using a software-only solution. I tried wiring the Cerbo relay only to the Master L1 AUX input, hoping to use the General Flag to sync the other 5 units. While I can select “Use General Flag” as a relay in the Programmable Relay (012C) assistant, the “General Flag” option is completely missing from the “Switch Conditions” list in that same assistant. I do see another assistant called “General flag user (013F)” in my list, but I am not familiar with it and I’m not sure if it’s what I need.

Is there anyone out there who knows this approach and could help me set up the assistants on this v560 firmware? I want to make sure the digital flag is stable enough for these 6 units to prevent any “Relay Test” errors (Error 8/11) without needing the physical 6-pole contactor.

Hi, I understand that there is no Assistant sequence that can take control of Realy AC-OUT 2 in the software area? Wiring AUX 2 to the Cerbo GX Relay would be the only solution!

Use an aux to signal a contactor to break the load and have ac2 out always on but have the contactor driven by your SOC conditions.

Break is after the combination disconnect.

Thank you, LX. This is a simpler solution. It is frustrating that it didn’t cross my mind, given that I already had all the necessary knowledge. I already have an AF96 3-pole power contactor available, so I will integrate it to break the load after the combination disconnect, using an AUX signal driven via Node-RED based on SOC and countdown.

No worries. sometimes we can’t see the forest for trees.

This is why the forum exists. We bounce ideas off each other so we can build awesome solutions.