Good evening,
within VE.BUS System Config / VEConfig I created two assistants to either turn off or turn on ACOut2 depending on Aux 1 input.
Apparently, this is not synced:
If I close Aux 1 on the L1 MultiPlus 2, only ACOut2 of that MultiPlus is turning off (and not ACOut 2 of the L2 or L3 MultiPlus).
Is there an easy way to “syncronize” that behavior across all three MP? Or do I have to tweak around with the Cerbo input and Node-Red?
So I wired all AUX 1 inputs together as suggested by @lxonline and it works flawlessly - all three ACOut 2 are working at the same time. If anybody is curious to know why I need it: I want to shut down a “stupid” inverter when the network operator sends a non-feed-in signal here in Austria.