48W of the DC load is DC loads to the boat, 100w of the DC load is inverter. The AC load is actually the DC/AC Skylla charger.
Essential loads should be the inverter but nothing shows. Is my load too small at 70va?
Any wiring on the AC output of an inverter will give a capacitive load, causing a small reactive current to flow, while the watts (Active - real - power) remains at or near zero.
This is perfectly normal.
You say the AC load is a skylla charger? what load is on the charger? if it’s charging a battery, but the battery is in float, then there is very little load.
Trying to set the ECO/AES mode as low as 14 W will be unreliable due to reactive currents with fixed wiring. Inverter current measurements at low values may be either positive or negative: there is usually some low level current indicated - resolution of the current sensors is not very high, and consequential power measurements can also be inaccurate at very low powers.
Hope this helps.