Installing a new smart shunt, I need to decide 500 or 1000A rating.
I have Epoch 12V 460Ah in parallel, 4/0 cables, and 250A class T fuses for each battery.
The fuses are sized such that the cables stay within their ampacity up to where the fuses will blow, at about 150% of rated current. We don’t have a lot of high-powered equipment, so the system is a bit oversized.
Is a 1000A shunt an unreasonable overkill? I assume you want keep the maximum system demand at less than 80% of rated current.