I have an Arco/Zeus install and Quattro is showing the battery temp as the alternator temp. So solar is sitting down because it thinks the batteries are overheating but they are not. Any thoughts on what I’m missing. Zeus is on the can bus to the Cerbo. Everything else reports correctly.
Under system set up, what is set to the battery monitor?
Does your house battery have a can connection to the GX?
In settings menu, find the DVCC settings and see if STS is turned on and what is selected. Even if it is off, try and turn it on and select the correct source or set as none. What firmware are you running, do you have a separate battery temperature sensor connected to the Cerbo or as @lxonline asked, CAN connected battery.