Hi, I’ve recently updated my setup from 3x Multiplus to 6x Multiplus, (as mentioned here ESS Speed of 6x Multiplus II way slower compared to 3x Multiplus II )
On top of the ESS regulation I now also see a strange behavior for peak shaving.
My understanding (from https://www.victronenergy.com/blog/2024/03/19/venus-os-v3-30-peak-shaving-for-ess/) of Peak shaving was that the ESS would see EVERY load behind my meter (not Multiplus (this is what is limted with the Grid current limit)) and adjust charging power to meet the defined “maximum import/export current per phase”.
I understood “There are two new AC current-limit settings, and those limits will apply to the complete system. Therefore they now include any high-power loads which are usually installed in parallel to the inverter/charger system such as EV Chargers and Heat pumps.” in the way that loads can also be on ACin1 and I also though my ‘old’ system did exactly that. ChatGPT is quite certain that only loads in ACout will be considered for peak shaving.
Can someone clearify this already ? (although this isn’t really my problem
)
For my testing today I moved all loads to AC-OUT, so peakshaving is somewhat similar to Gridlimit (all all current has to go from AC-IN1 to AC-OUT)
Why I need peak shaving
I have a 50A (~34kW) main breaker, can charge my batteries with 24kw (6x4000W) and have 2 EVs which can charge with 11kW and 7.7kW and a heatpump that usually runs around 2kW + house loads. So I can easy kill my breaker.
My settings
Peak shaving is enabled (and can’t be disabled for some odd reason (but I’ve read multiple times that is ‘normal’ right?) and for this test set to 25A
25A => ~17kW
for this test I’ve also set the grid limit to 32A => ~22kW
Switching to “keep batteries charged” leads me to ending up at
having L1 already go over the 25A
So: 32A Grid | 25A PS = 28/19/29
activating one car charger (car + heatpump + loads → 18kW)
now we’re running already at 32A or ever slightly higher
So: 32A Grid | 25A PS = 28/19/29 → 32/18/33
when I reduce the grid limit to 25 doesn’t effect the 32A
reducing the peak shaving to 20A
finally some effect .. we’re reducing to 27ish A
So:
32A Grid | 25A PS = 28/19/29 → 32/18/33
25A Grid | 25A PS = 32/18/33
25A Grid | 20A PS = 25/15/27
I thought this was running spot on with my old 3x MP2 setup .. why is this so off with the 6 MP?
Am I doing something crazy wrong? Any Idea? I’m running the latest stable firmware and VenusOS and the ESS assistant is up2date
Any help / idea is welcome, Thanks
Kolja
PS: also fancy
30A are sometimes 5.5kW and sometimes 8.5kW ![]()
(I’ve double checked with dbus-spy and the Wattage is correct .. not sure where the Amps are coming from)