Passtru on Grid
How can I activate passtru on Grid (AC Input 1) for my load?
I have a client who doesn’t want to charge from the grid. Want to charge with PV during the day and Gen set at sun set.
Thank you
Can you detail the system, wiring and configuration please.
Not nearly enough to go on.
If you are using ESS you can set an inverter limit of 0W which forces passthrough.
Or force minimum soc that is sufficiently high enough.
Beta now properly supports a minimum of 100%
Hi Nick,
45kVA Quattro programmed 3Phase
PV Inverter assistant
Grid charge set between 15% to 80% (Programmed Relay)
Gen charge between 12% to 50% (Programmed Relay)
New development:
Client want to stop charging from grid, to activate passthru. Gen set charge only when there grid outage/collapse
If you have an actual grid connection, the easiest is to move to the ESS assistant, then use schedules, limits and probably nodered to help automate this.
This isn’t out of the box behaviour.
Typically passthrough and charge only is what goes together by default.