Hi,
Recently installed my Victron system (1x MultiPlus-II 48/5000/70-50, 4x Pylontech US5000-1C - 48V 4.8kWh, 1x Cerbo GX MK2, VM-3P75CT energy meter)
I have 3 fase grid 25A. My Victron is connected via AC in on L1. I don’t have anything on the AC out.
Every Saturday, when my wife starts to get cooking and fires up all possible appliances at the same time, I get multiple Overload messages. I don’t understand why the Victron tries to give more then it’s capable of or even how to understand this error message. Any help or ideas would be appreciated!
In dynamic ESS I have the following configured:
- Can you sell energy back to the grid? Yes
- Maximum import power: 17 kW
- Maximum export power: 17 kW
- Operating mode: Green mode
- Battery energy capacity: 18 kW
- Maximum discharge power: 4 kW
- Maximum charge power: 4 kW
In VEConfigure I have these settings:
- General
- 50Hz
- AC input limit: 25A (Overruled by remote)
- Enable battery monitor: Yes
- State of Charge when Bulk finished: 85%
- Battery Capacity: 400Ah
- Charge efficiency: 1.00
- Grid: Belgium C10/11 ed.2.1:2019-09
- Inverter
- output voltage: 230v
- DC input shutdown: 44V
- DC input low restart: 48V
- DC input low pre-alarm: 48V
- Charger:
- Enable Charger: Yes
- Lithium Batteries: Yes
- Charge current: 25A
- ESS Assistant
- LiFePo4 with other type BMS
- battery capacity: 400 Ah
- Sustain voltage: 48V
- Cut off voltage: 46V
- Inverting is allowed when voltage rises: 1.2V
- PV Inverters on AC out: No
In the console I have these settings:
- Multiplus: Grid current Limit: 25A
- AC input 1: Grid
- Position of AC loads: AC input only
- Monitor for grid failure: Enabled
- ESS:
- Mode: Optimized without battery life
- Grid metering: External meter
- Multiphase regulation: Total of all phases
- Minimum SOC (unless grid fails): 20%
- Limit inverter power: off
- Grid setpoint: 50W
- Grid feed-in: AC-coupled PV-feed in excess
- Peak shaving: Always
- Limit system AC import current: Yes
- Max import current (per phase): 17A
- Limit system AC export current: Yes
- Max system export current (per phase): 17A
- DVCC: shows ‘forced on’ but disabled.
- Limit charge current: off
- Limit managed battery charge voltage: on
- Max charge voltage: 55V
- SVS - shared voltage sense: Forced off (disabled)
- STS - Shared temperature sense: Forced off (disabled)
- SCS - shared current sense: disabled
- Controlling BMS: Automatic selection
- Auto selected: Pylontech battery