Ongrid in Spain

We have a system in Spain, a Victron 10,000 multi-plus, with a BYD LVS 8.0, alsoconnected to the Spanish grid.
In Spain, the grid operates with so-called potentia.
During the day, we can draw 3300 watts and at night 2500 watts.
When the grid is turned on, the green “Inverter On” light on the multi-plus starts flashing.
The limit on the multi-plus is set to 11A. Did I make a mistake here? Please advise.

What is the question? Is the system working as intended?

In any case a 10,000 multiplus with a 8.0kWh battery seems oversized, see BYD documentation.

ThX, just wondering why the inverter led is flashing with the grid ON, and yes later we have to extend , a extra battery.

If it looks like this....

Then it is power assisting.
If you download the victron toolkit you can look up led definitions if you don’t like using the manual

Power assist happens when the inout current limit is below the load being drawn or when solar is assisting loads in an ess system

Ahhhh, now clear to me THX al lot !