Existing off grid system is as follows -
- 3 x 48V/15k Quattros in 3 Phase - Switched as a group.
- Cerbo GX
- 110kwh of BYD Lithium.
- 4 x 450/200 MPPT RS.
- 3 x 5kw SMA Sunnyboy MPPT’s on the Quattro’s AC Output’s controlled w/ frequency shifting through the PV Inverter Assistant (1 x Sunnyboy on each phase).
- Single phase 16kva Generator powering a 15k MultiPlus-II as a charger only onto the DC bus (networked to Cerbo w/ MK3 interface).
I had planned to add another 5kw Sunnyboy to L1 (2 in total on this phase, 1 on each of the other phase’s) - The PV inverter assistant mentions to that “each phase must have the same solar power installed” - What are the implications of not following this? Being that the AC coupled solar is a variable charge source between phases, I can’t understand how this is an issue?
I also plan to upgrade the single phase generator to a 3 phase unit into each of the Quattro’s - How does frequency shifting on the AC Output work when the Generator is running? Do I just program the generator to stop at around 95% SOC to allow the Quattro’s to be able to frequency shift, to throttle back the Sunnyboys when required?
Thanks in advance.