I’m setting up a 3-phase system with 3x Quattro 48/8000 and pylontech batteries with MPPT’s only.
I’ve setup the CCGX so that the relay is used for generator start/stop. The CCGX relay then activates another relay that supplies each Quattro with 1-phase on AC-1-IN.
But …
When the CCGX activates the relay (based on SOC), the 230V appears on the VE-bus of each Quattro but these don’t start charging the batteries.
It worked for about a month or so without any problems but now all of a sudden it doesn’t anymore. I’ve reset the complete system blank as a 3-phase system but it just doesn’t work.
Then used assistants, identical in all 3 Quattro’s
generator general flag to ignore AC-IN
generator start/stop
=> use general flag
=> open relay to start
=> start when SOC < 10%
=> stop when SOC > 20%
=> generator not stopped by AC-IN
This does not work to start charging batteries either.
Anyone any idea what is happening or what could cause this problem?
Whatever % the batteries are on … it never starts charging.
There is no generator connected. I use the grid as a “generator”. When I activate the “generator” on the CCGX, the grid voltage appears on the AC-IN of all Quattros (VE bus indicates 230 Volt, 50 Hz) but the Quattro doesn’t start charging.