Can you check the settings of the multi via VE Configure and/or Connect ? …
I suspect that the charging voltage in the “Absorption Mode” is too high … possibly also an old setting of the lead batteries …
This may cause the two BMS of the batteries to go into ‘fault’ mode and disconnect the connection …
Normally, you need an MK3 interface to access the Multi via the VE bus. You also need the ‘VE-Configure’ software.
Since you do not have a GX in your system, there is no other way to configure your Multi.
At the moment, you are probably using the standard configuration of the multi… For the use of LiFePo batteries, it is essential to adjust the settings.
That one one thing I changed, the installer left all the dip switches set to off, I found in the documentation to set DIP 2 to on.
The system is 4 years old, I started having problems with the 2x100Ah battleborn, so got bigger batteries and went LiePo4 at 280AH each with 200Amp BMS.
After swapping out and changing the capacity to 560Ah, I started seeing this with a “bare DC” system. That is I left the house buss and the Solar disconnected to check the system.