Hello,
I have a problem and hope that someone can help me with a practical solution:
I have installed a Multiplus II off-grid system in a vacation home and now have a problem:
The system is often left unattended for weeks at a time, and power outages are common in this area. My set SoC limit is 15%.
However, if the power outage lasts too long, the SoC of the battery continues to drop. If AC power does not return, the battery pack with its BMS goes into protection mode at 2.5 volts cell voltage. Internally, the MOSFETs disconnect the output, i.e., the Victron also switches off. In this protection state, the battery can last a very long time.
Now comes the real problem: when (at some point) AC power is restored, the Victron Multiplus II switches on and could now recharge the batteries. However, the circuit breaker (MCB) of the AC supply regularly trips immediately during the relay test, which starts after about 1 minute in the Multiplus II. The inrush current must be extremely high; this is a 16 A fuse (B characteristic).
This happens reproducibly; I have recreated it independently in two locations. Reinserting the fuse does not help either; it blows again during the next Multiplus relay test. Only when a functioning battery is connected to the DC battery input again can it connect to the AC side without any problems.
Does anyone know of a practical workaround? A setting that precharges the coil or tells the Multiplus to be “careful”?
Thanks!