I could use some help with my setup – been stuck on this for about a week now.
Issue: My Multiplus II stays in bulk mode even though the Pylontech batteries are already full and showing Idle (around 50.01 V, 0 W). From what I understand, it should normally move on to absorption and then float, right?
Setup:
Multiplus II 48V/5000VA/70A
2 × Pylontech US5000 (4.8 kWh)
Lynx Distributor
Cerbo GX mk2
No Victron BMS, just using the built-in Pylontech BMS over VE.Can.
Settings (based on Victron’s guide):
ESS mode: Optimized (with BatteryLife)
DVCC: Max voltage 52.4V, STS/SVS/SCS all off, BMS control = Pylontech
Absorption: 52.0V, 1h
Float: 51.0V
Am I missing something in the configuration, or misunderstanding how this should behave?
I can post screenshots from VE.Configure or the GX console if that helps.
If you would like the system to act as ess, you should set a lower minimum soc
When you want the batterys to be full and only use them for backup, set it to keep batteries charged
with a new system it can take a while (days/weeks) for all batterys to balance, if its a new system setting it to keep batteries charged will also help to balance
The batteries are at 99% at 50v. There is something is not happy there.
Since you have programmed as recommended i would remove the voltage cap. leaving the voltage cap on can cause problems. Sometimes it is best to leave the batteries to sort themsleves out.
Have a look at the CCL they are requesting in the parameters. If it is not 0A they want to be charged.
Basically leave them to charge up fully over a day or two. Let them settle down.
Not always the case on an ess system with bms control.
They are trying to balance. They are able to sort themselves out. So leave them to do so.
As a side not ESS is in bulk production when solar is covering loads thebulk state does not necessarily mean the battery bank is in bulk.