Hi,
I’m checking an installation with a MultiPlus-II 48/5000/70-50, 8 * Pylontech batteries (total 400Ah, 48V), firmware v3.54 .
We’re not able to get this system charged for more than 63%.
We’ve tried:
- setting min SOC = 100%
- grid-feedin to a high value
- setting: optimised without battery-life
- equalisation
- scheduled charge levels
No high-voltage alarm is raised when charging, low-voltage warnings are raised when discharging.
Actual CVL=53.2V CCL=165A DCL=200A.
Battery temperature: 23°C
In VE.configure:
Battery monitor:
- charge when bulk finished: 95%
- Battery capacity 400AH
- Charge efficiency: 95%
Charger: - Curve: fixed
- Absorption: 52.4V
- Float: 51V
- Charge current: 70A
When we ‘play’ with the settings, we can manipulate the system so the battery discharges and charges. But at SOC=63% , 51V, charging stops.
Last SOC above these values date from summer 2025, the system has not been changed since then.
Any idea what is happening? All suggestions are welcome.
Thank You,
Luc.
Additional information, all batteries are detected by Victron, no modules are blocking charging or discharging.