Hi team,
I need some assistance with the PowerAssist feature.
I have a client that want’s to add an addtional 180kW of peak loading to their site (site supply limit is 180kW).
I am trying to work out if 12 x 15kVA Multiplus II in ESS mode would achieve this.
If the inverters are installed in Parallel to the grid/site loads on the “input” side of the external transfer switch, will this cause any issues with the PowerAssist function?
Will the powerAssist function still function with parallel inverter units? (there is a table for peak PowerAssist output, but I assume that is per inverter).
By logic, it would be feeding any load after the CT if the transfer was closed.
Since the whole set up just injects into the system (almost like an ac pv inverter) though why would the loads be before the transfer switch and not after? Are you trying to do critical and non critical?
The transfer does what it says, transfers the load from the primary source to the loads like a ups. (So replaces the internal ones in the inverter same function.)