Hello everyone,
I need help diagnosing a grid-loss issue with the following system:
- MultiPlus-II 4k5
- 1 × Dyness DL5.0C Pro, 51.2 V / 100 Ah
- SmartSolar MPPT 150/45
- ESS installation
During some scheduled grid outages in Ukraine, the MultiPlus-II goes into Off for around 10–30 seconds, causing the lights and other loads to lose power briefly. The unit then restarts and enters Inverting mode.
VRM reports Low Battery and High DC Ripple, although the battery voltage remains around 52.7–53.3 V, the state of charge is normal, and the load is only a few hundred watts.
The problem appears only during some scheduled outages and has not been reproduced by manually opening the AC input breaker. Sometimes the voltage relay ZUBR turns the grid off due to high input voltage (>260) without issues for MP2, which instantly goes to inverting mode.
My settings are: grid code other, ups function on, dvcc activated, LOM B.
The difference between MP2 battery measurement and BMS is ~0.10 - 0.15v.
DC Ripple in reality is from 0.00 to 0.2v, usually ~0.1v.
I initially installed the system in March with a MultiPlus-II 3000 VA GX, and I did not experience any problems with it. However, there were no scheduled power cuts during that period, so this comparison may not be conclusive.
The battery was connected using the cables supplied with the Dyness battery. Around September, I replaced the 3000 VA inverter with the current MultiPlus-II 4.5 kVA.
Could anyone help diagnose what may be causing the MultiPlus-II to enter Off during grid loss and report Low Battery and High DC Ripple, despite normal battery voltage and a relatively low load?
I would appreciate any suggestions regarding further diagnostic steps or possible solutions. I can provide detailed VRM data, VE.Bus logs, screenshots, the VEConfigure file, and Dyness BMS parameters if required.