My name is Giuseppe Basilio Rudiger, from Chile. I did my first ESS installation as a backup system for an office, MultiPlus-II 48/6500, Cerbo GX, Pylontech Fidus 16 kWh battery, load around 450 W, no feed-in to the grid.
Since the beginning of the installation (July 13) the AC OUT 1 output has shut down about 7 times, at different periods of time, always close to a grid disturbance. It lasts about 2 minutes and the Cerbo reboots every time, and also there are records of clean grid outages that it transfers perfectly, even one of 2 hours.
I tried firmware v557 to v560, config with and without ESS, a voltage regulator upstream, battery firmware twice, ground relay measured and correct. And the most drastic thing was changing the inverter for another one from the same batch HQ2537 and the next day it failed the same, this time when the grid came back after a real outage.
My hypothesis is that the problem seems to be the BATCH or the model, and not my installation. This week I will install a MultiPlus-II 5k, to see how it behaves.
Has anyone with a 48/6500 from that batch seen the same with ground relay enabled and v560?
MultiPlus-II tested = (S/N (HQ2537GQ4VQ and HQ2537MEU7E))
I have data (my own logger at 1 second, separate from the Cerbo, that is why you see what VRM does not record), CSV, portal and events recorded. I can send by private message.
Regards
“Grid outage, 4 minutes inverting fine, collapse when the grid comes back”