My setup is 3x MultiPlus-II 48/5000/70-50 for a 3-phase system, and a Cerbo GX. Software version is 3.66 on the cerbo and v558 on the MultiPlus’ses, Updated today from 3.60 and v498, but the issue is the same.
Everything works fine until the incoming AC fails. Then it switches to battery power, but after about a minute, it switches off with “#10 System time sync error”. I understand that according to VE.Bus error code list (sorry, can only put 2 links in a post…) this error is usually a ‘by product’ of other errors, but in this case, its the only error i get. After about 10 seconds the error disappears and the system powers on again. Only to fail again in the same way after 10 - 30 or so seconds. This keeps repeating.
When i disconnect the converters from the Cerbo, it works. If i connect it via an MK3 to my laptop, or the cerbo, it works. When i plug it back into the direct VE.Bus connector on the Cerbo, it fails again.
It looks identical to whats described in Lost Grid followed by VE.Bus Error 10: System time synchronisation problem - VictronEnergy , but there the work-around seems to be to use the MK3, but i was just told in Inverter Data not showing on GX Display - #12 by pwfarnell this is not supported (anymore?) and converters connected via the MK3 are seen as secondary.
The battery are 6x 4.8kWh Pylontech. When i tested it, the load on the system was about 400W, and they batteries where at 40% SoC.
Grid code is for The Netherlands.
Anyone can help me resolve this issue? i would like to use the system as a backup for the house.
Thanks!