Hello everyone,
I have a new system, installed 2 months ago: Multiplus II 6k5, single phase + AC Coupled Huawei + one Dyness Battery. Everything works fine with one glitch.
The problem is that, after a grid fail the grid remains disconnected indefinitely.
So I am basically draining my battery and staring at the sun ![]()
I am reading the parameters via ModBusTCP from the Victron and plotting charts in Grafana. From these charts I can tell that, after the grid comes back:
- The voltages are correct at the grid
- The frequency is correct at the grid, a solid 50.1 Hz
- Victron continues sending frequency signals to the Huawei on the AC out periodically. I see this as spikes in my charts at some 10-20 seconds interval
- This is in line with the manual that says, that the frequency shift cannot be maintained when the grid is reconnected because the Multiplus must use the same frequency
- The grid is NEVER connected. I have waited one hour, two hours and nothing happens
I have found this topic Stuck on Disconnected & Discharging even w/ Grid Meter Showing Power where the user said that they have reverted to a previous version of the GX Firmware and that fixed the issue.
I don’t want to go back to another firmware because I have just bought my Multiplus II and installed the latest firmware.
I have access to the SSH and have / can make traces via dbus-spy and dbus-monitor. From those traces I can see that the grid is “available”, but there is something that periodically tells “ignore the grid”. That something is one of the agents.
I only have a single agent, an ESS through which I configured the AC coupled inverter (the Huawei which holds the solar panels).
I have exhausted all Gen Ai out there looking for a way to debug this thing, so I am reaching out to the community and the the Victron staff.
I repeat: This is repeatable behaviour (pun not intended). I can trigger it, literally with a switch, so I think this is a golden opportunity to find the bug in the ESS / GX / wherever this comes from.
The only way I have found to get out of this “stuck” situation is to go in the HTML interface of the Multiplus and set the mode to “keep batteries charged”. This seems to snap the Multiplus from its dreaming and forces a reconnection to the grid. Once that happens, I switch back to my “Optimized without battery life” and the system is back to normal. But … I cannot be looking at the charts constantly waiting for the fail to happen.
In short:
a) how can I fix this?
b) Victron staff: I am available with any information. Let’s fix this bug.
MultiPlus-II 48/6k5/100-50
FirmwareBuild 3.79 20260826152305
VE.Bus version: 2602560