Hello everyone,
I have a question regarding the Victron MultiPlus 2 15kVA. I read that it cannot be set up in parallel with six inverters, two on each phase. Could anyone clarify whether this is possible or not?
I believe you need an extra switch that can switch of the 30kVA of power. Alternatively you could get 6x 5kVa inverters. Their internal switches are synchronous and powerfull enough to allow for 30kVA of power.
the extra switch i something we buy from victron ?
The sources don’t really go well, but I think the most important information is there:
In the last document they mention the following transferswitch is required in Europe:
Ziehl relay UFR1001E required
Dont use chat gpt, its not allowed per community guidelines
2 Likes
See this 3phase and parallel setup for more info
There is a link in there to the specific setup with 15k multiplus inverters, see:
You could also use quattros they support parallel in big systems