Hello all!
I’m about to install a pv array with battery storage due to grid problems in my home.
Although a multiplus II 5000kva could suffice, I’ve gone on the safe side and I’ve got 2 5000s set up in parallel.
My first pv array during the winter will not be sufficient so I’ll have to use/charge from the grid or a 5kva generator.
If there a quick and easy way to change the power in limit for Grid or genset? The grid has about 3.5kW limit and the generator has the 5k.
I have a Cerbo S GX and its relay outputs and digital inputs are still available.
I already have set up a couple of contractors for selecting the grid/generator inputs.
I’m a full newbie on the cerbo programming for any functions… Its been a ruff few weeks and I only got the power cables a couple of days ago so it’s all un-done yet
I’m just collecting information on the details here and there. I’ll be sure to post my system and set-up when I get it wired in
(I’ll have tome for testing from the start since I still have to correct the house breaker panels - I’ll just have the hot water, my PC and well pump while testing)
I’ve read a little bit on the red node programming for bat SOC and charge on demand… I’m not sure of its the way to go.
I also have a PLC that will control a few water, power usage and other systems.
It could activate the grid charging if I can have a ‘low bat’ signal out of the cerbo or something.
Any input will be useful on the multiple automatic configuration if it’s possible.
and noting came up so I’m not sure if I was not clear about something and I’m surely going to need some time testing the thing out
I think this is what you are after. All the really useful stuff is locked from node-red programming. See if this is applicable.
The same setting is probably fine for both the grid and generator (assuming it doesn’t put out a dirty sine wave)
You will never pull 5kVa from a 5kVa generator.
They are rated at sea level (so factor in de rating for altitude) and usually don’t want more than an 80% load anyway.
I’ll have a read about this further. I’ve seen node red so this could help out.
thank you
I’ve never load tested the generator but I’m pretty sure I’ll never load it to full. If I ever need to use it for recharging bats is would be at a lower setting but not as low at the grid connection.
my grid connection will have to support my sisters mini-house (heating mainly) and its a 3.45kW line… I would probably can pull 2kW from it maybe just 1.5kW. as for the generator I could pull a “little” more.
(after testing further I can be sure and will probably add force cooling on it for long use sessions)
I’m pretty near sea level. 120/200 Meters higher or something like it. it should pull about 4Kw out of it fine…
thank you :slight_smile:
Ok. Well then also be aware that not loading the generator enough is also bad for it.
You will definitely need to experiment balancing two households. :+1:
yes. its a gasoline model. I’ll have to load test it and try to see. I’m expecting to pull a little under 4kW out of it and see how it actually behaves.
I’m going to have a read on the transfer switch thingy on github ^^
edit: /typo…