ok but of a left field question..
have a Cerbo GX, multiple MPPTs and a 48/15000/200 connected to a bank of 5x100amp, 10kWh LiFePO batteries.. Grid connected, planning on ESS/NodeRed .. all good, sill building but don’t expect any issues… however also have a 6kVA backup generator that i would like to bring into the mix for extended power outages..
So i can’t run an ATS and change over because the 15000 will overload it, so was thinking of a charger to the batteries.. however this is another issue as there don’t appear to be any 48vdc 100amp chargers available that would also be compatible with the GX so everything is aware… until i thought to myself, “could i use a multiplus in charge only mode?” .. hence the question above.
So to clarify, can a Multiplus II 48/5000/70 be connected to the same battery bank as a 48/15000/200 with the generator as its AC input to provide a 48vdc by 70amp charging supply?
Thanks in advance.
Michelle