Multiple bugs when using VM-3P75C meter as solar yield meter

Hi,

I have to following setup:
3x MultiPlus without gridmeter, AC IN 1 connected straigt to the GRID and AC OUT to my home.
2x VM-3P75C energy meter between AC OUT and solar panels grid connected (roof and shed) configured with PV inverter role on OUTPUT.
1x DC Smart Shunt for backup generator feeding directly into battery
1x Lynx shunt between battery and MultiPlus / Generator
1x Cerbo GX running beta and large image

Cerbo GX C00A HQ22442UZ4T v3.70~61 v3.70~61 Up to date
MultiPlus-II 48/5000/70-50 2623 Unknown v558 v558 Up to date
Lynx Shunt 1000A VE.Can 141 0331645 HQ23114CQRN v1.10 v1.10 Up to date
SmartShunt 500A A389 HQ2249HQXVK v4.19 v4.19 Up to date
Energy Meter VM-3P75CT A1B1 HQ2517AAAGC v1.11 v1.11 Up to date
Energy Meter VM-3P75CT A1B1 HQ25177D7W6 v1.11 v1.11 Up to date

The Current Clamps are connected as shown in the manual, because of feeding back power from Solar to Grid the displayed values are negative.
Is this correct of do i need to change the direction ?

On VRM portal the DC load / generator is missing.
The current flow of the PV is from the grid to the PV inverters.
No correct device names displayed.

On Remote console the DC load / generator is present.
The PV inverter is at the INPUT side instead of the OUTPUT side.
The current flow is correct.
No correct device names displayed.

Thanks for your advise, if needed you can reply in Dutch.

Kristian

I changed the direction of the Current Transformers and now it seems right.
Except that the Solar Generator is still projected at the INPUT side instead of the OUTPUT side on the Remote Console.

So the LOAD is your home and the SOURCE is the Solar generator. (makes sense)