Id guess the PV power is split between battery and grid since the grid current is hitting the 6A limit. So any leftover is charging the battery. And by chance thats roughly 50/50. So whats your gridsetpoint set to? If you set that to -2000W for example, it will always feed back to grid up to those 6A grid current limit.
Whats the charging shedule for, do you have cheap power in that window?
Yes, it is 50/50 by chance. At first I thought everything was fed in until there was more solar.
Grid setpoint is 0W.
During those hours power is very cheap. Hence feeding makes no sense.
The documentation for the Multi RS Solar states for “Optimized without BatteryLife”: “when there is enough solar power to satisfy the loads, then the excess solar power will be used to charge the battery.”
Since there is no statement in the ESS-section that this would reverse (which would be very odd), I assume it remains true (which is logical).
Hmm, disabling feed-in. A provoking question. Makes me think. Perhaps I should find the places where feed-in can be disabled and toggle them all once. Could give a hint of where the problem can be.
GX is latest version: v3.85. I might as well try rebooting; it is a computer after all…
When weird issues persist, and since you mentioned DESS, if all else fails, sometimes following the cerbo factory reset procedure (used to be chapter 9 iirc, but don’t hold me to it) is also a useful step to rule out a latent problem.
I will be very reluctant to do that since there is no proper configuration management (I am aware of), I must reconfigure everything by hand, which is error-prone and time-consuming. I am afraid it will only take me further down the rabbit hole of not knowing which setting to touch & being unsure if settings work properly. So, yeah, really a last, last resort. (And I will be forever masking the bug of course.) This is my personal system, but I wouldn’t even think about doing that one other’s systems…