MPPT 75/15 Showing voltage but no current
I have a set-up with 6 panels and 6 MMPTs. Worked fine for for best part of a year, now one is showing Volts but no Amps. Looking at history, this one has been on and off whereas others have been consistently on. I have seen older posts about a battery temp reading being the issue, but I don’t have that feature.
Any help much appreciated
![IMG_3836|231x500](upload://bTKU66K
Z7kFIoCImHda3xfilsPW.png)
Post a Victron Connect screenshot of the mppt’s detailed history.
Common mppt no charge issues.
Bad panel, bad connection between panel and mppt, maybe a bad fuse/breaker between the panel and mppt .
Or perhaps the fuse in the bottom of the mppt is kaput,or a fuse between the mppt and battery.
Sounds like a similar problem I had recently with one of my MPPT chargers.
Turned out to be a problem with the MC4 connectors
Could you maybe swap around the panel/charger connections to see if the issue moves with panel or stays with the charger? A process of elimination?
Also, do you use any of the cheap torpedo shaped DC breakers? I had a problem some years ago where they would drop voltage under load, despite not getting warm. Only used quality Durite breakers since then with no more issues.
Thanks. I have added screenshots to my post. This morning, its working again. Very strange
Thanks - The cabling is very (too) tight and there isn’t enough room to change them as suggested. I don’t think there and any MC4 connectors