I was reading the manual of lynx bms (7. Commissioning and Operation of the Lynx Smart BMS) and it mentions the transition from off mode to on mode:
If the Lynx Smart BMS was off due to low cell voltage or low SoC shutdown, it will exit OFF mode and return to ON mode when
- it detects a charging voltage >11.7V (>23.4V for a 24V system or >46.8V for a 48V system) than the battery voltage on the system side or
Am I reading it correct that if I have a 12v battery, the charging voltage needs to be at least 12 + 11.7 =23.7 v to “wake up” the bms?
In addition, a fairly recent (2022) post by victron staff (Lynx Smart BMS still needs Battery protect? - VictronEnergy) said the lynx bms contactor won’t automatically reconnect:
In addition, a BatteryProtect switches off at a voltage to be defined and switches on again at another voltage. The Lynx Smart BMS does not do this
Did anything change after that post?