Is upgrading Solar DB MCB from B50 to B63 acceptable/worth it to increase AC charging?

I’m looking for advice from Victron installers and electricians regarding upgrading the AC supply protection to allow higher battery-charging power during my 3-hour low-rate window.

System overview

  • Inverter: Victron MultiPlus-II 15 kVA (48 V)

  • Batteries: 3 × 15 kWh Fogstar (total 45 kWh)

  • PV:

    • South: 10 × 470 W (4.7 kW)

    • North: 11 × 470 W (5.17 kW)

    • West: 9 × 470 W (4.23 kW)

  • DNO export limit: 12 kW

  • Home annual usage: ~4100 kWh

Current charging performance

During my 3-hour off-peak period, the inverter charges the battery at around 10–11 kW, shown as approx 180–200 A DC on the Victron graph.

This matches the breaker installed in my Solar DB:

  • Proteus XL50BRK B50 (50A)

So the 50A MCB appears to be the bottleneck, limiting AC input to around 11.5 kW.

What I want to achieve

I’d like to increase charging power into the batteries so they reach a higher SOC within the 3-hour cheap tariff.
Upgrading the breaker from B50 → B63 (or possibly C63, depending on cable spec) should enable about 14–14.5 kW AC input, giving ~13–14 kW DC charging.

My question

Is it acceptable and safe to request that my electrician upgrade the breaker to a B63, given that the DNO export limit is already set to 12 kW and the breaker only affects AC-in charging (not export)?

I want to confirm:

  • Do you agree with upgrading the Fues to increase the AC charging?

  • Whether upgrading the MCB conflicts in any way with the DNO export limit

  • Whether the MultiPlus-II can safely use 63A AC-in on a single phase

  • Can this be done by any installer or does it have to be the original installer. In case the original installer is not available.

No, an MCB does not limit current. I just turns off when the current is too high.

The multiplus II 15000 is rated for up to 200A DC charging, it looks like you’re at the maximum.