Incorrect / Inaccurate Current and/or Power Readings on ET112 Grid Meter

Hi, I have an ET112 on my grid-connected setup connected to my cerboGX, however, the current values are being presented in the VRM Portal and on the cerboGX seem to be a lot higher than the power figure being represented.

Does this mean losses are in play here because the current is true and the power is a “calculated value” or is it potentially somethign else.

My setup consists of a cerboGX, MultiPlus-II, ET112, Fronius AC-Out tied Inverter and a MPPT SCC with a 48V battery conected via BMS-CAN.

I was thinking of adding a smart shunt to the battery to assist in better SOC measurements, but I’d be open to any advice here.

Cheers.

The difference in VA and power at the grid meter display will be due to a poor power factor, and the low current.
The difference in the VRM display can be due to a time lag (up to 15 min) or averaging of the values.
You will get more accurate tracking of battery voltage and Soc from a smart shunt than with the Multiplus.