But what i dont understand is: the ET112 grid-meter is installed immediate after the Main MCB, so it knows the total sum of all loads. Is it not like this that While there is enough PV power , this PV power should be used to power the AC loads, the battery should not be discharged. I thought this was the main idea of ESS with a gridmeter?
Yes it sees the SUM of everything.
If you have 1kW PV and 1kW load the ET112 sees nothing.
The system doesn’t know that there is a PV inverter.
If you know you have 2kW PV, 1kW into the battery and the ET112 shows 0W → you have 1kW loads.
But again, the system doesn’t see that because the loads are supplied directly from PV.
You need another ET112 to measure the PV production.
Then the system knows the PV, grid, battery and AC OUT and can calculate the AC loads.