The AC-Input of L1 is “way off”.
- The Solaredge is reporting 2169 Watts
- The Inverter on L1 is measuring 1368 Watts.
And that is about the difference of -785, as my thought outlines.
So, what I see, that your system also says “0” Consumption on L1. A wonderful 0 is very suspicious, that indicates that a “negative” consumption is calculated, and therefore displayed as 0.
From the Data - and the assumed connection paths - The system should conclude: 2169 Solar, 1368 into the multi and 6W to grid, the consumption musst be (2169-1368-6) = 795 - which again is the value we are missing on the AC In side.
Data shows, it is connected to ac-out of L1. But eventually it is configured to report it’s feedin on AC-IN? Then, the maths for consumption would conclude -1368 consumption and just display that as “0”.
And for the grid, what happens then is:
- Sum of phases by the multi is 1370+1455-6 = 2819
- But there is 2169 Solar reported on AC In, so total Grid-Value is 2819-2169 = 650
Can you check, that your solar inverter is configured to be connected to AC-OUT?
Settings → PV Inverters → Inverters - make sure that is set to AC-OUT.
If that IS Set to AC-Out: Change it to AC-In, save, wait a couple of seconds, then change it back to AC-Out to make sure the setting propagates again through all involved services and stuff.