Does anyone have an idea why the data is incorrect? PV production is not equal to consumption + injection.
3 fase grid with EM540 meter and PV inverter on fase L3 with ET112 meter + Multiplus
Thanks.
Does anyone have an idea why the data is incorrect? PV production is not equal to consumption + injection.
3 fase grid with EM540 meter and PV inverter on fase L3 with ET112 meter + Multiplus
Thanks.
A single multiplus will always assume it is running on phase 1.
So, what will happen is, that the Grid-Meter is reporting something totally different for phase 1 than the MP measures (Because it is connected to phase 3) - and the difference will be considered AC Load.
Best would be to move the multiplus to phase 1, so these values align properly.
ok, thank you very much!
If you expand a bit more you will probably see phase compensation working there as well.