Wrong data in VRM - PV production is not equal to consumption in 3 phase system

Does anyone have an idea why the data is incorrect? PV production is not equal to consumption + injection.
3 fase grid with EM540 meter and PV inverter on fase L3 with ET112 meter + Multiplus

Thanks.

A single multiplus will always assume it is running on phase 1.

So, what will happen is, that the Grid-Meter is reporting something totally different for phase 1 than the MP measures (Because it is connected to phase 3) - and the difference will be considered AC Load.

Best would be to move the multiplus to phase 1, so these values align properly.

1 Like

ok, thank you very much!

If you expand a bit more you will probably see phase compensation working there as well.