Please help, did my research, watched video, read the manual and still perplexed.
Multiplus 12/2000/80-50 120V 2765 on v481 firmware. (yes, I know its old and I did update to v556 after all my testing was complete so didn’t have a chance to see if it had an impact).
Generator is a Westinghouse igen2550
Air Conditioner that overloads is a Coleman Mach 3 13.5k unit with Coleman softstart.
Battery is 280 Ah Lithium
Settings:
Multiplus switch in the 1 position. I did not do anything to any dip switches.
AC1 input current limit of 29.0 Amps
Dynamic current limit ON
Accept wide input frequencies ON
AC low disconnect 90V; high 140V
Ground relay ON (even though I’m using a bonding plug because of a Progressive Industries surge unit installed on-board
Charger Enbled and set to battery specs.
AC Input Contorl all OFF
When I’m on shore power, everything opperates as expected. Air Con working, microwave too… When the generator is connected, power is supplied and all works well. Even microwave operates. When the Air Con fires ups, the I can hear the Multiplus click and fan comes on briefly, then the unit displays an “Overload” error. When monitoring the display, I did notice that VA jumps to 1850ish. The generator does kick up for a brief moment then falls back to low idle once Multiplus shuts down.
Thoughts… My soft start is garbage and I need a MicroAir. Or hopefully one of my setting is off.
Any help would be highly appreciated.
-Boris