Hi Everyone. I have MPII ESS with Cerbo GX. I just updated to FW to 3.81 hoping the display inconsistency would be fixed. GUIv1 is correctly displaying the grid and solar. GUIv2 is adding the solar yield to grid. VRM agrees with GUIv1. I think there is a wrong calculation in GUIv2 (I’m not a programmer!) GUIv2 doesn’t realize the loads are being powered by the battery and the solar is exported.
You don’t need to be a programmer everything is set up in the GX itself.
What is the position of the fronius in the physical set up?
Then what is its assignment position on the GX?
What is set to meter the grid input in the set up?
Hi.
The Fronius position is AC Input 1
The assignment on GX is Grid
Grid metering is Inverter/charger (there is no energy meter)
Is the load position set to output only or both input and output?
They should be the same, but just double-check the new UI settings are consistent. Shouldn’t be possible not to be, but never hurts to confirm.
Hi Nick. It is the same.
This will be why there is a problem.
For fronius installed on the input a grid meter before the fronius should be installed.
There is basically no way for the system to actually know what is being drawn in at the grid before the fronius.
Notice in the system example with the AC PV on the input that there is a grid meter. See paragraph 3
It seems like it is connected over modbus, as the PV is identified as Fronius.
Won’t change the fact that with an AC PV inverter on the AC input, there needs to be a grid meter for the readings to be correct.
I am trying to understand why GUIv1 and GUIv2 are different. There are no loads on the ACin side of the MP, only the Fronius. The Fronius is connected via modbus TCP to the Cerbo. I used a clamp meter to confirm the current readings shown by GUIv1 and VRM. I could put an energy meter on the grid side but it would only show what I can already see on GUIv1. This installation uses the MP to power essential loads only - all on AC out. Non essential loads are on the second phase. I did consider putting the Fronius on AC Out but the MP is not approved for grid feed-in in Australia.
AI content moderated as per community guidelines.
That’s the point.
It only knows the AC input at its terminals.
What is doesn’t know (and it could be guestimated) is the actual input power at the grid point which is what the grid metering is supposed to be.
All the system as it stands knows is that the fronius is producing, it is being told that it’s terminals are the grid (which it is not actually) not it is trying to reconcile with an X factor where the power is going.
Either way the Victron was manual is clear, if there is an AC PV on the input there should be and there is expected to be a grid meter. In short it is not being used in the expected or recommend way. Nothing will be right.
The system is configured as you currently have it, to read the grid here… And it is the only place it can actually read.
When you have the fronius now connected over modbus and it is trying to control it there can even be further issues.
Is there a fronius meter there as well?
OK. So you are saying that VRM and GUIv1 is wrong?
A CT from the multi is also acceptable, though the EM will allow for better system response.
The AC PV is detected by the GX and sends all of the usage data to the GX, the older and newer UI’s clearly seem to be behaving or displaying data differently.
Sounds a bit counter-intuitive that the correct values could be wrong, it may be the case that they are getting it right by mistake. You would expect consistent reporting across all of the surfaces. I have asked for clarification, though there is no guarantee any will be forthcoming.
If a grid measurement of sorts is required then there is little that can be done to escalate the different behaviour.
There are many Fronius inverters, and plenty of other brands as well, all reporting correctly but using meters.
The old UI is also not being developed any further so won’t inherit any changes that the newer one will.
The numbers should be consistent across interfaces so the new UI is having a maths problem, that will be added to the todo list but a meter is still required and would resolve the issue.