System:
Quattro as ESS
Generator connected to AC in1
Grid connected to AC in2
Standard loads connected to AC in2
Fronius Symo connected to AC in2
Critical loads connected to AC out
No DC MPPTs
When the generator runs under load once a month for testing, the Quattro switches the power to the critical loads. The grid continues to supply the normal loads. The current generated by the Fronius Symo (AC in2) charges the batteries and feeds into the grid if necessary.
This is how it should be.
However, when the batteries are full, the Fronius Symo is throttled down, even though it is connected to the grid input AC in2 rather than the generator input AC in1. If the control is switched off by disabeling “sunspec,” the battery voltage rises above the set value until the BMS shuts down.
For a Multi with only one input, this behavior would be correct.
DC MPPTs, if present, would also have to be throttled down.
With a Quattro, however, the system does not take into account that it has two separate inputs and that these can be configured differently.