Hi LX, I’ve tried to set the limit om 10A as well. The system just doesn’t take the loads in front of the MP’s into account. When I put everything on ACout the peak shaving works flawless.
Yes I did update everything to the latest versions. No beta.
In the mean time I found this posting from @SmartVolt : Grid current limit exceeded with DESS and peakshaving on - #3 by SmartVolt And indeed that seems to work. Only problem is that when you have only loads on ACin configured in system setup, you won’t find the menu self-consumption from battery in ESS. So I went to system setup, said system has loads on both sides, went to ESS → self-consumption from battery, put in on all system loads. Now it works. After I went to system setup and putting it to loads only on ACin the menu item self-comsumption from battery disappeared again but it still works now.
Is this a bug?